Visitor874
Price$3.69
1. Wide input voltage range 4:1, isolated regulated output 5W
2. Isolation voltage 3000VDC
3. Transfer efficiency up to 86%
4. Quick Start:300mS(Typ)
8. Input undervoltage protection, output short circuit, overcurrent protection
General Features
| Project | Operating conditions | Min. | Typ. | Max. | Unit |
| Insulation voltage | Input-output, test time is 1 minute, leakage current is less than 1mA | 3000 | -- | -- | VDC |
Insulation resistance | Input-output,insulation voltage : 500VDC | 1000 | -- | -- | MΩ |
| Isolation Capacitor | Input-output,100KHz/0.1V | -- | 20 | -- | pF |
| Operating temperature | Reference temperature derating curve | -40 | -- | +85 | ℃ |
| Maximum temperature of the shell during operation | -- | -- | +100 | ||
| Storage humidity | No condensation | 5 | -- | 95 | %RH |
| Pin soldering temperature | The solder joint is 1.5mm away from the shell, 10 seconds | -- | -- | +300 | ℃ |
| Switching frequency | PWM mode | -- | 250 | -- | KHz |
| Viberation | 10-55Hz,10G,30Min.alongX,YandZ | ||||
| Shell material | Aluminum shell | ||||
| Minimum time between failures | MIL-HDBK-217F@25℃ | -- | 2X10^5 | -- | Hrs |
| Input current (full load/ no load) | 24VDC Input Series | 3.3V | - | 211/5 | 220/12 | mA |
| others | - | 251/5 | 260/12 | |||
| 48VDC Input Series | 3.3V | - | 106/4 | 110/8 | ||
| others | - | 150/4 | 155/8 | |||
| 110VDC Input Series | 3.3V | - | 43/0.3 | 45/0.5 | ||
| others | - | 56/3 | 58/8 | |||
| Reflected ripple | 24VDC nominal input series, nominal input voltage | -- | 40 | -- | mA | |
| 110VDC Input Series | -- | 25 | -- | |||
| Impulse voltage (Isec.max) | 24VDC Input Series | -0.7 | -- | 50 | VDC | |
| 110VDC Input Series | -0.7 | -- | 180 | |||
| Starting voltage | 24VDC nominal input series, nominal input voltage | - | - | 9 | ||
| Input undervoltage protection | 24VDC nominal input series, nominal input voltage | - | - | - | ||
| 48VDC nominal input series, nominal input voltage | - | - | - | |||
| 110VDC nominal input series, nominal input voltage | - | - | - | |||
| Startup time | Nominal input voltage and constant resistance load | - | 1 | - | mS | |
| Remote control terminal(Ctrl)* | Module turned on | Ctrl floating or connected to TTL high level (3.5-12VDC) | ||||
| Module turned off | Ctrl is connected to GND or low level (0-1.2VDC) | |||||
| Input current at shutdown | - | 6 | 1 | mA | ||
| Note: *Ctrl control pin voltage is relative to input pin GND | ||||||
| Ripple & Noise | Pure resistive load, 20HMz bandwidth, peak-to-peak | -- | 80mVp-p | 120mVp-p | - | 80mVp-p | 120mVp-p | |
| Startup delay time | - | 300ms | - | - | 1s | - | ||
| Output voltage regulation | Input voltage range | - | No adjustment end | - | - | No adjustment end | - | |
| Dynamic response step deviation | 25% nominal load step | - | ±3.0% | ±5.0% | - | ±3.0% | ±5.0% | |
| Dynamic response recovery time | - | 300μs | 500μs | - | 300μs | 500μs | ||
| Output overvoltage protection | Full voltage range input | 110%Vo | - | 160%Vo | ||||
| Output overcurrent protection | Full voltage range input | 110%Io | 150%Io | 200%Io | ||||
| Output short circuit protection | Full voltage range input | Sustainable, self-healing | ||||||
Note: ① For product models with output voltages of ±5VDC and ±9VDC, under 0%-5% load conditions, the maximum output voltage accuracy is ±5%; ②When tested under the working conditions of 0%-5% load, the index of the load adjustment rate is ±5%; ③0%-5% load ripple & noise less than or equal to 5% Vo. Ripple and noise test method Twisted pair test method, you can add capacitive load at the output to reduce light load ripple. | ||||||||